How do we cool a server rack that's sharing a room with solar inverters?

November 16, 2026 4 answers
Asked by _c82!marmotfunnel.6

Our server rack shares a room with solar inverters that put out a lot of heat. A mini split had repeated coil failures, and a small replacement cooler failed after a couple of months. Moving the rack could be costly. What should we look at before buying another cooling unit?

Answers

6d!ticketratchet_293

Get an HVAC contractor to calculate the load and investigate the failures before replacing anything. Repeated coil problems don't tell you by themselves whether the unit was too small, had an airflow issue, was set too cold, or had some other fault.

Give them the inverter specifications and operating data, plus measured rack power if you have it. The calculation needs the heat released by the inverters, not simply their total electrical output, as well as the rack and other room loads. Ask for a system sized for the expected peak conditions and continuous operation.

Neravi+8d:

It would also help to tell the contractor what temperature the equipment manufacturers allow. A target of 65 degrees Fahrenheit may be lower than the room needs.

Reply to this answer
v.519+modladle

Price a rack move as well as a proper cooling installation. It might be expensive, but keeping two major heat sources together can mean paying for a larger system and dealing with the same problem whenever cooling fails.

If there is another suitable room, compare the cabling, electrical work and downtime against the cost of cooling this one. A backup cooling unit is worth discussing for whichever location you choose.

Reply to this answer
n.347!socketladle

Ask whether ventilation can remove some of the inverter heat before it reaches the rack. An exhaust fan or ducting might help, but it needs a proper path for replacement air and somewhere suitable to discharge the heat. Just dumping hot air into a ceiling space isn't automatically a good solution.

Reply to this answer
4z!canvaswicket_583

A small portable cooler is a risky substitute for equipment designed to cool a server room around the clock. In particular, a single-hose unit can exhaust conditioned room air and draw warmer replacement air back in. Have the contractor compare a properly sized split system with commercial spot cooling equipment, based on the actual room and heat load.

Reply to this answer