Our sensors are currently at the top of the racks on the hot aisle side. Is that the best place to monitor temperatures, or should we also be measuring the cold aisle?
Should temperature sensors go in the cold aisle, hot aisle, or both?
Answers
For equipment protection, start with the air entering the servers. Put sensors at the rack fronts where the intakes are, ideally at the bottom, middle and top. The top can catch warmer air recirculating from the hot aisle.
Set intake alarms against the requirements for your equipment. ASHRAE's commonly cited recommended intake range is roughly 18 to 27 C, but check the applicable guidance and equipment specifications before choosing thresholds.
Reply to this answer
Both sides are useful if you have enough sensors. Compare intake and exhaust temperatures over time to see the temperature rise across the equipment and spot changes in airflow or load. A hot aisle reading by itself is harder to interpret because it's measuring air after the equipment has heated it.
I wouldn't apply a cold aisle intake threshold to the hot aisle. They answer different questions.
Reply to this answer
If probes are limited, prioritize intake locations over a neat, symmetrical layout. Cover different heights and pay particular attention to spots where hot air might leak back toward the rack fronts. A sensor at the bottom alone could miss a warm pocket higher up.
Reply to this answer
Check what your cooling units and equipment already report before buying more probes. In-row coolers may expose readings through SNMP, and equipment temperature monitoring can add useful context. Discrete intake sensors still help show the conditions around the racks, while humidity sensors can provide another view of the room environment.
Reply to this answer
Add your answer
Answers are reviewed before publication.
_m37!plendori.5:
So the existing hot aisle sensors can stay, but they shouldn't be the only temperature alarms?
8c+fablecrank_294:
Right. Exhaust-side readings won't necessarily tell you what air is reaching each server intake.